I have a cod question on out door street lighting.
Sounds fishy to me.
It is spec'd a #10 on the prints. No OCPD on the load end, other than fuses at the fixture.I suspect that the engineer specified 1/0 AWG conductors and they were installed as 10 AWG conductors... However is there any chance that these are 'outside taps of unlimited length'?
If the #10 is protected at the load end at 30A, and the #10 is outdoors, then this might be compliant.
-Jon
Ok, i see what you are saying. Thanks for the info....Actually as far as the NEC goes, those are magnetic ballasts not transformers, they would be subject to article 410, such as 410.138, not 450.
Your # 10 conductors must be protected at 30A per 240.4(D)(7). The protective device must be located per 240.21(A) or (B).
This is an old light system tied into a new light system..That's been the 'unspoken fix' for longer than i've been around
~RJ~
He is, just trying to save accusing somebody of something, then getting corrected. Some people don't take that very well. LOL But, sounds like he is right.I would suggest going back to your installer, engineer, or general contractor if you think you have an issue.