m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Jun 2, 2019 #1 Just thought, do we have any technical objections of having outgoing cables larger than main cable due to voltage drop?
Just thought, do we have any technical objections of having outgoing cables larger than main cable due to voltage drop?
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Jun 2, 2019 #2 m sleem said: Just thought, do we have any technical objections of having outgoing cables larger than main cable due to voltage drop? Click to expand... No objection. But improving the voltage drop to the level required might require upgrading the main/feeder/home run cable too.
m sleem said: Just thought, do we have any technical objections of having outgoing cables larger than main cable due to voltage drop? Click to expand... No objection. But improving the voltage drop to the level required might require upgrading the main/feeder/home run cable too.
M MAC702 Senior Member Location Clark County, NV Jun 2, 2019 #3 No different than having the long run of larger cable upstream of a disconnect, and "normal" cable from disco to machine.
No different than having the long run of larger cable upstream of a disconnect, and "normal" cable from disco to machine.