al hildenbrand said:I assume this is a walkin cooler, in a non-dwelling occupancy.
That said, take a look at 210.8(B) for the short list of required GFIs. Until more detail is provided, I'm not sure that you are required to install GFIs.
wonder said:I have a customer who wants to install some general use utility outlets inside their walkin which is used for vegatable reasearch. As long as they are GFCI and wp in use covers, any problems?
mdshunk said:I wire walk-in's just like outdoors, due to the way they're washed down. In normal use, the air inside a walk-in is fairly dehydrated.
iwire said:Many times I think the use of bell boxes makes matters worse, if your not dealing with wash down issues. The coolers I work on rarely (OK never :rollget hosed down.
If you going to use WP methods maybe small drain holes would be a good idea.