hmspe
Senior Member
- Location
- Temple, TX
- Occupation
- PE
Just checking to see if I'm overlooking anything. I have an out of state design project that's adding a cell tower at a mini-storage. The mini-storage has 3 buildings, and I'm guessing from the pictures at mapquest.com that the building this goes in is supplied by an outside feeder. I have asked the client to confirm. They was a separate service for the cell equipment, which will be in one of the storage spaces. NEC 225 says only one outside feeder. NEC 230 says only one service. I'm not finding anything that prohibits one outside feeder plus one service. I think it's a very bad idea to have both an outside feeder and a service, and I think the intent of the code is to have one or the other, but I'm not sure it's a code violation based on the actual text. Any thoughts?
Martin
Martin