Outside Service Connectors

Status
Not open for further replies.

cdb277

Member
Location
Virginia
I have a state inspector saying that I need waterproof connectors between my panel and meterbase. They are mounted side by side, with a short piece of PVC and (2) TA's with standard rings. I'm using the bottom knockouts, which are well below the connection points. We have always installed services like this and for the life of me I can't find the code section saying this is legal. Help would be appreciated.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree the inspector is off base on this. Once you are below the buss bars then it is not an issue.


312.2 Damp and Wet Locations. In damp or wet locations,
surface-type enclosures within the scope of this article shall be
placed or equipped so as to prevent moisture or water from
entering and accumulating within the cabinet or cutout box,
and shall be mounted so there is at least 6-mm (1∕4-in.) airspace
between the enclosure and the wall or other supporting
surface. Enclosures installed in wet locations shall be weatherproof.
For enclosures in wet locations, raceways or cables entering
above the level of uninsulated live parts shall use fittings
listed for wet locations.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with the others not required since it's below the live parts. If it were a box then he would be correct, maybe he was thinking of that.
 