gottabewired
Member
- Location
- dyersburg tn
i recently installed a disconnect on a service i built, thwe specs are:
3 200amp ch panels inside with mains, and a 600amp non fuse disconnect out side the wall approx 2 feet behind the panels , i use three barrel lugs
with 3/0 thhn and the neutral lug kit to match. the question is, the inspector said i have to use a fused disconnect. the service intrance conductors from a ground mounted transformer were supplied by the power athourity, 350 alum.
parrallel. the nec according to article 230.70 part vi does not state that this disc. has to be fused. am i way off or am i missing something. next the inspector tells me that i dont have to have a disc. out side and that i can just put the feeders in a trough and let the power company make their connections there. the only delima i have there is where to make the grounding connection other than a block mounted in the trough. blah
cornfused ,ever heard of this?:-?
3 200amp ch panels inside with mains, and a 600amp non fuse disconnect out side the wall approx 2 feet behind the panels , i use three barrel lugs
with 3/0 thhn and the neutral lug kit to match. the question is, the inspector said i have to use a fused disconnect. the service intrance conductors from a ground mounted transformer were supplied by the power athourity, 350 alum.
parrallel. the nec according to article 230.70 part vi does not state that this disc. has to be fused. am i way off or am i missing something. next the inspector tells me that i dont have to have a disc. out side and that i can just put the feeders in a trough and let the power company make their connections there. the only delima i have there is where to make the grounding connection other than a block mounted in the trough. blah
cornfused ,ever heard of this?:-?