Outside Work

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Don't do a lot of underground work. This explanation may be too simplistic but wondering if you thought of time required for this install makes sense. Just want to make sure I'm not way off base. Thank you.

Scope. Area is 70'x70'. Most all work is underground with PVC schedule 40 and RGS elbows and XHHW wire.
All work fed from NEMA 3R panel
All work is 3/4" conduit except control panel feeds.
All excavation, backfill and restoration by others.
Mounting of control panels by others.

1. Install 600A panel and supports.
2. Run a feed to each auger control panel about 30' each - 2" w/ 3 #3/0 and 1 #6
3. Install (3) duplexes on low wall and (1) in storage container.
4. Install and feed Misc 20A loads in storage containers. Mostly roll up doors with push button.
5. Install and feed (4) 15' light poles(aluminum). Not bases. Also ground rod at each.
6. Install (3) 8' surface fixtures in storage containers with switching.

I come up with about (2) men 12 days. This is for 7 hour days. Looking at it I think this is very much on the high side.




1703866549816.png
 
Don't feel bad. I'm an engineer and I tried to argue with NYS Education that ground rods should not be required at light poles. I was overruled and told they need to be there. They have not been responsive when I asked for support documentation.
 
Ground rods are the "Holy Grail' of electrical work, don't just pound one, I always pound at least two on each project for good measure just to be safe !
 
Ground rods are the "Holy Grail' of electrical work, don't just pound one, I always pound at least two on each project for good measure just to be safe !

I have the ultimate ground rod hammer, it's called the "Monster Hamer". I can drive ground rods from morning to night !Milwaukee Manual - Rotary Hammer_Page_01.jpgMilwaukee Manual - Rotary Hammer_Page_02.jpgMilwaukee Manual - Rotary Hammer_Page_03.jpgMilwaukee Manual - Rotary Hammer_Page_04.jpgMilwaukee Manual - Rotary Hammer_Page_05.jpgMilwaukee Manual - Rotary Hammer_Page_09.jpgMilwaukee Manual - Rotary Hammer_Page_06.jpgMilwaukee Manual - Rotary Hammer_Page_10.jpg
 
Why aren't ground rods needed at light poles?
Not to mention all of the other comments, but if you think about this an electrical piece of equipment... what benefit does the ground rod serve? If you have wired the system up properly, there should be a grounded a conductor as well as an equipment grounding conductor which should carry current back to the source and trip the breaker in the event of a fault. And, if everything is bonded correctly, every light pole should be continuously bonded to one another.
 