Here is something from Vince
Why We Need To Increase The Equipment Grounding Conductor
MR. SAPORITA:··Vince Saporita, Saporita
The panel action may have brought about some ·· · unintended consequences.··Larger phase conductors installed for reason, not just for voltage drop, will result in greater available short circuit currents. · Greater available short circuit currents result in greater currents that must be safely carried by the equipment grounding conductor underground fault conditions.··If too much current flows over the equipment grounding conductor, it will overheat to the point where it begins to anneal.··When that happens, it will no longer be tight under the lug after if cools back down.··When that happens, the ground return path is no longer adequate.··The next ground fault may not be cleared by the over-current device, allowing for the worker that touches the case of the equipment to be electrocuted.··This concept is not new.··It was published decades ago and detailed in the IAEI book on grounding.··The point at which the equipment grounding conductor will no longer be tight under the lug is called its validity rating, and it can be calculated.··Look in the IAEI book on grounding if you want to make the calculation. I urge you to vote for this motion, which may prevent the unintended consequence of an electrocution of an electrical worker.