journeyman0217
Senior Member
- Location
- philadelphia,pa
I am currently working on running a new 13.2kv circuit underground. It will be installed in schedule 80 PVC and 24" below grade (will be under a roadway) according to table 305.15a. I do not see anything requiring this install to be concrete encased. The only thing I see anywhere requiring concrete encasement is where non-shielded cables are used and these will be shielded cables. On the other hand, I have come across this same install in the past and it has always been encased in concrete. Am I missing something in the code somewhere...or is this just a job specific requirement per the design engineer??