No, that is not a "it helps" situation. It's a deal breaker. If the load is 761 amps or higher, then a pair of 500's is a code violation. Furthermore, if you don't actually have a load calculation, if you do not know whether the load is above or below 760, if all you know is that the OCPD is 800 amps, then IMHO a pair of 500's is still a code violation. The violation is in article 316, not 240.. . . yes 500?s (paralleled) are compliant on an 800A OCPD, it helps that the load does not exceed the allowable 760A