Carultch
Senior Member
- Location
- Massachusetts
PS: A combination EGC/GEC is still treated as a GEC. Only difference is that it is permitted to terminate to the poco-side grounding bus, rather than using an irreversible connection. One gets to be creative if there are multiple inverters connected to the other end. :angel:
Correct. It is seen as a conductor that has to follow all rules pertaining to both the EGC and GEC.
The practice I've learned as a recommended way to do this is as follows:
For circuits that have a #6 EGC or smaller, it makes sense to run a combined EGC/GEC.
For circuits that have a larger EGC, run a separate EGC and a #6 GEC. Trying to combine the EGC with the GEC is "asking for trouble". Because it becomes much more difficult to irreversibly bond larger sizes of wire, and follow all the other GEC rules.