mdshunk said:
Isn't the old rule of thumb (if one even believes that rules of thumb exist), that oil-filled transformers can be overloaded 140% almost continuously as long as certain temp limits were not exceeded? After all, isn't that what the Thermotell is all about?
I don't know that I would word it like that but if you can keep it cool enough, you could probably load it more than that.
With auxiliary cooling, you can increase the capacity. For example, my power transformer table (not all-inclusive) has:
OA = oil-immersed, self-cooled
FA = auxiliary forced air
FOA = auxiliary forced oil & air
so for a transformer with OA/FA cooling:
For 2500 kVA and below = 115% of the OA capacity.
For 2501-9999 kVA 1ph or 2501-11999 kVA 3ph = 125% of the OA capacity.
For 10000 kVA 1ph or 12000+ kVA 3ph = 133% of the OA capacity.
and for a transformer with OA/FA/FOA cooling:
For 10000-16667 kVA 1ph or 12000+ kVA 3ph = 133%/166% of the OA capacity.
You can overload otherwise but probably not continuously. You would have to look at ambient temperature, temperature rise, capacity factor, pre-loading, reduced life allowance, etc.