Hey guys, joining this conversation a bit late, but having some similar issues with my Mitsubishi system. All the low voltage boards have been fried twice now. I'm on my third set but am keeping the system off until I know I have solved the power quality issues.
Measuring 249V from the power company, but additionally have a 9V phase imbalance (129V on A and 120V on B). Mitsubishi states that a phase voltage imbalance should be <3%. You guys have not been mentioning above if you see a phase imbalance.
My system works fine until there is a power outage, then all the low voltage boards are fried. No bad fuses, no breakers trip, and no surge protectors are tripped, which is odd. I have seen voltages as high as 252V transiently. I have a "Ting" circuit monitor on the higher of the two legs that consistently reads 128V average with spikes above 132V.
I recently jackhammered three deep holes in solid rock to add three grounding plates associated with two structures. The neutrals had multiple places where they were tied to ground. My electrician reduced that to only one place on the site where that is supposed to happen. No improvement to the phase imbalance. It does however go away when there is no load (home off, guest house off, PV array off). It returns as I add loads from individual circuits, with no obviously failing circuit. It just scales with load. Electrician identified at least four splices in the drop between my transformer and the house.
Austin Energy claims there is no issue at their end and that 250V is within power specifications. They are likely testing without load. I am pushing back and trying to get them to change taps at the transformer to reduce my voltage down to 240V. I think I am the only house on this transformer.
Did the buck/boost transformer help solve your problem? I'm thinking of installing that or an isolation break transformer and adding a grounding rod dedicated to the heat pump alone to get it separated from the power quality problems that otherwise are not disturbing anything.
The sensitivity to phase imbalance seems to be a design weakness in addition to the 253V maximum voltage specification. I'm also considering converting the unit to 120V operation to work around the weaknesses. Thoughts?