240.4(C) Overcurrent Devices Rated over 800 Amperes. Where
the overcurrent device is rated over 800 amperes, the ampacity
of the conductors it protects shall be equal to or
greater than the rating of the overcurrent device defined in
240.6.
240.6 Standard Ampere Ratings
(A) Fuses and Fixed-Trip Circuit Breakers. The standard
ampere ratings for fuses and inverse time circuit
breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50,
60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300,
350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000,
2500, 3000, 4000, 5000, and 6000 amperes. Additional
standard ampere ratings for fuses shall be 1, 3, 6, 10, and
601. The use of fuses and inverse time circuit breakers with
nonstandard ampere ratings shall be permitted.
(B) Adjustable-Trip Circuit Breakers. The rating of
adjustable-trip circuit breakers having external means for
adjusting the current setting (long-time pickup setting), not
meeting the requirements of 240.6(C), shall be the maximum
setting possible.
if the calcuated service load is 840 amp what size overcurrent device is required
if the calcuated service load is 840 amp what size overcurrent device is required
You would need to know how much of the load is continuous and how much is non-continuous to answer that question.
He said 'the calculated load' if that was done using article 220 that is already taken care of.
An adjustable trip breaker could be used, but you cannot use the "next size up" rule for OCPD selection for sizing the conductors.
IOW, if you use a 1000A breaker, your conductors must have an ampacity of 1000A.
Yes, he said 'the calculated load.' There is NOTHING in Article 220 about continuous vs. non-continuous load. It is not part of calculating the load.
So you're saying that whether it's continuous or non-continuous is irrelevant to this thread.
You would need to know how much of the load is continuous and how much is non-continuous to answer that question.
I'm saying exactly the opposite.
If the load calculation said that the calculated load is 840 amps isn't that good enough to answer the question in the OP?
But again the OP stated: "the calculated service load is 840 amp" why would you need any more information to answer the question? If this were a test question are you saying that it would be unanswerable?
I don't know another way to say it...a calculated service load per Art. 220 would not indicate what portion of the load was continuous and what portion was non-continuous.
This is odd to me as we were taught in trade school that doing a 'load calculation' would include the continuous and non-continuous loads. Examples D3 and D3a both seem to bear that out. Or in other words if you havent included both types of loads you have not done a 'service calculation'.
David, it seems you are proving my point for me. A 'service calculation' as the op mentions includes both continuous and non-continuous loads.
Let me try this...
The Calculated Service Load in Annex Example D3 is 118.3A (28,400VA @ 120/240V.)
What is the minimum size OCPD required?
Are you in the 2011?