OK I'm having a problem with a plan check sitting on my desk.
I have two 30kva 208-480 3 phase transformers. One is feeding a 17.8 kva A/C unit and the other is feeding a 14.4kva A/C unit.
One is being fed with a 70 amp breaker (3 #4) and the other is being fed with a 50 amp breaker (3 #6)
When I check my cheat sheet and run the calcs I come up with a minimum 83 amps of protection required.
Am I missing something or is the engineer mistaken? I'm guessing that because they sent out the wrong voltage A/C units and that the pipe has already been run (1") that they are trying to make the wire fit.
I have two 30kva 208-480 3 phase transformers. One is feeding a 17.8 kva A/C unit and the other is feeding a 14.4kva A/C unit.
One is being fed with a 70 amp breaker (3 #4) and the other is being fed with a 50 amp breaker (3 #6)
When I check my cheat sheet and run the calcs I come up with a minimum 83 amps of protection required.
Am I missing something or is the engineer mistaken? I'm guessing that because they sent out the wrong voltage A/C units and that the pipe has already been run (1") that they are trying to make the wire fit.