I'm preparing a class concerning Branch Circuits, Feeders, and Services. In an effort to illustrate the similarities and differences among the three, I've either missed something (most likely), I don't quite understand something (also fairly likely) or the code has a hole in it.
Concerning conductor sizing, the following indicate that conductors shall have an ampacity of 125% of continuous and 100% of non-continuous loads:
210.19(A)(1)(a)
215.2(A)(1)(a)
230.19(A)(1) (service entrance conductors)
The code specifies similar requirements for overcurrent protection for conductors and equipment in:
210.20
215.3
But I can't find any such requirement for service equipment in Article 230 Part VII (or part VI for that matter even that is only for disconnect rating).
I understand that 230 Part VII protection is for the OVERLOAD portion of overcurrent protection only but that seems most applicable to the requirements of 210.20 and 215.3 since g.f. and s.c. currents would be greatly in excess of the 125% and 100% ratings required.
What am I missing?
Concerning conductor sizing, the following indicate that conductors shall have an ampacity of 125% of continuous and 100% of non-continuous loads:
210.19(A)(1)(a)
215.2(A)(1)(a)
230.19(A)(1) (service entrance conductors)
The code specifies similar requirements for overcurrent protection for conductors and equipment in:
210.20
215.3
But I can't find any such requirement for service equipment in Article 230 Part VII (or part VI for that matter even that is only for disconnect rating).
I understand that 230 Part VII protection is for the OVERLOAD portion of overcurrent protection only but that seems most applicable to the requirements of 210.20 and 215.3 since g.f. and s.c. currents would be greatly in excess of the 125% and 100% ratings required.
What am I missing?