It is not possible to provide short circuit and ground fault protection at the load end of a conductor. The only protection that can be provided for service conductors is overload protection as that can be at any point on the conductor and still provide the required protection. Most utility systems do not provide any protection for the service conductors. Short circuits and/or ground faults on service conductors typically have to "burn" open to clear the fault. The is one of the reasons for the more robust bonding that is required for service equipment and raceways.I'm preparing a class concerning Branch Circuits, Feeders, and Services. In an effort to illustrate the similarities and differences among the three, I've either missed something (most likely), I don't quite understand something (also fairly likely) or the code has a hole in it.
Concerning conductor sizing, the following indicate that conductors shall have an ampacity of 125% of continuous and 100% of non-continuous loads:
210.19(A)(1)(a)
215.2(A)(1)(a)
230.19(A)(1) (service entrance conductors)
The code specifies similar requirements for overcurrent protection for conductors and equipment in:
210.20
215.3
But I can't find any such requirement for service equipment in Article 230 Part VII (or part VI for that matter even that is only for disconnect rating).
I understand that 230 Part VII protection is for the OVERLOAD portion of overcurrent protection only but that seems most applicable to the requirements of 210.20 and 215.3 since g.f. and s.c. currents would be greatly in excess of the 125% and 100% ratings required.
What am I missing?