I would appreciate some input on the required overcurrent protection for a fire pump motor installation as I describe below.
A fire pump controller, which has a transfer switch , is being supplied from a utility transformer with an unfused disconnect being inserted between the transformer and controller. The conductors from the unfused disconnect are terminated to a 150 amp circuit breaker on one side of the transfer assembly. The other side of the transfer assembly, which is another 150 amp breaker, has conductors connected to it which originate at an on site generator. My question is this; Does the overcurrent protection for the fire pump motor have to be capable of carrying the locked rotor current of the motor for an indefinite period of time? Article 695 of the NEC is somewhat unclear to me. I'm trying to apply 695.4 (A) of the 2005 NEC to make this call.
Thanks in advance for any comments.
A fire pump controller, which has a transfer switch , is being supplied from a utility transformer with an unfused disconnect being inserted between the transformer and controller. The conductors from the unfused disconnect are terminated to a 150 amp circuit breaker on one side of the transfer assembly. The other side of the transfer assembly, which is another 150 amp breaker, has conductors connected to it which originate at an on site generator. My question is this; Does the overcurrent protection for the fire pump motor have to be capable of carrying the locked rotor current of the motor for an indefinite period of time? Article 695 of the NEC is somewhat unclear to me. I'm trying to apply 695.4 (A) of the 2005 NEC to make this call.