Delcobob
Member
- Location
- Oklahoma City
I have a typical set up for a transformer. I have a 277/480V panelboard with a 3P100A breaker feeding a 75 kva 480V - 120/208V transformer. The secondary side has 3/0 copper conductors (less than 10' long) feeding a 200A 120/208V 42 ckt panelboard. I have always installed a 200A main breaker in the low voltage panel for this installation. Now I have an engineer that tells me the main is not necessary, according to 450.3. I see his point, but I still insist the main is required as per 240.21 (C). Can anyone shed some light on this situation for me? Thanks.