- Location
- New Jersey
- Occupation
- Journeyman Electrician
Basically the NEC does not care if you plug a #16 AWG extension cord into a 15 or 20 amp receptacle circuit. The NEC only cares about the listing of the cord as outlined in 240.5(B)(3).
It does not say that you can or you cannot. I cannot find it and you haven't been able to find it either because it doesn't exist in the NEC. As you stated in the OP 240.5(B)(3) is as close as you can get. If the extension cord is listed and has a 15 amp plug on the end then it can be used on either a 15 or 20 amp circuit. It would help if the NEC explicitly stated the requirements (20 amp circuits) like it does for field assembled cords sets in 250.5(B)(4) in 250.4(B)(3) but it does not.
I don't have access to UL817 so I can't comment as to whether or not that will answer your question. Is this question related to a specific application?
Not sure 240.4(B) would apply. I would think not because of the statements in 240.5
I disagree with your interpretation, the NEC doesn't say that, it leaves that to the listing which allows a 15 amp molded attachment plug suitable for a 15 or 20 amp circuit. 240.5(B)(4) says that if you make the cord in the field then the #16 gauge conductors are just fine on a 20 amp circuit so why should a manufactured cord be any different? You seem to be searching the NEC for some justification for your conclusion that doesn't exist.Actually the NEC very clearly states one can NOT use a 16 AWG extension cord (which is clearly listed / labeled at 13 amps) where it is protected at 15 or 20 amps.
2020 NEC 240.5(B)(3) says: "Flexible cord used in listed extension cord sets shall be considered to be protected when applied within the extension cord listing requirements." The extension cord is listed at 13 amps, not at the plug rating of 15 amps. The label on the extension cord says 13 amps, UL 817 says 13 amps.The rating of the plug is inconsequential in this.
So far no one has been able to show me how that logic is incorrect.
At the risk of being another tome, to the OP, I would suggest finding what code cycle 240 B 5 3 was added, and then getting the supporting proposals and comments from the NFPA
I disagree with your interpretation, the NEC doesn't say that, it leaves that to the listing which allows a 15 amp molded attachment plug suitable for a 15 or 20 amp circuit. 240.5(B)(4) says that if you make the cord in the field then the #16 gauge conductors are just fine on a 20 amp circuit so why should a manufactured cord be any different? You seem to be searching the NEC for some justification for your conclusion that doesn't exist.
I agree, as I stated earlier in this thread the NEC doesn't really care about a manufactured extension cord, the section relating to them in the entire 1000 page book is a mere 22 words. They've punted anything beyond what you've stated to the NRTL that lists the cord.If the manufacturer put a 5-50R molded plug on the the 16 gauge cord it wouldn’t be listed and I don’t think you’d find it at Home Depot. Its listed with the 15 amp plug. The manufacturer has passed liability to the consumer by labeling it 13 amps and the NEC is okay with that because a short circuit on a 15 or 20 amp circuit won’t spontaneously burn up the extension cord and a continuous overload will have been caused by the consumer ignoring the manufacturers instructions for loading.
The title of this thread says "extension cords".Okay I did not read everything closely so I am wondering what the application is in the scenario you are asking. Is it for a motor? If so then the overload protection in the motor is protecting the cord from overload while the breaker is protecting it against short circuit and ground fault.
If this is not field assembled then the manufacturer has had the assembly tested and it is listed as such. I am assuming the load on the cord is not more than 13 amps. Otherwise Imo there is enough info given by everyone where it shows this is not an issue.
To me the phrase "when applied within the extension cord listing requirements" is a reference to the load which may be connected to the cord, not the breaker protecting the receptacle into which it is plugged. Both interpretations (yours and mine) are consistent with the grammatical structure of the sentence. But my interpretation allows such listed cords to actually be used and yours does not (since 13A fused receptacle circuits are AFAIK non-existent).
I know that logical analysis often is not the best tool to apply to understanding the NEC, but in this case the fact that extension cords appear to have been allowed by regulatory authorities for a long time leads me to look for an interpretation the allows that.
You answered it right there.when applied within the extension cord listing requirements.
yes and it has also mentioned cord sets.... Honestly knowing more of the situation would be better. I have seen motors connected with cord and plug. Isn't that a cord setThe title of this thread says "extension cords".
After 40 posts IMO we're not discussing anything other than an extension cord.yes and it has also mentioned cord sets.... Honestly knowing more of the situation would be better. I have seen motors connected with cord and plug. Isn't that a cord set