Correct me if I’m wrong.
For a single continuous load of 16.7 amps (16.7 X 1.25 = 20.8 amps) is it still permissable to size the overcurrent protection at 20 amps using 12 awg thhn conductors with 75 degree terminals (conductor is then rated for 25 amps)?