How do you know the load is 16.7 amps if you can't read the label? Most water heaters- I assume residential- are 4500 watts and are 240 v--- that means 18.75 x 1.25 = 25 amps minimum conductor and 30 amp max overcurrent protective device.
If this is commercial and the load is rated 4500 watts at 240 and the actual voltage is 208 then you could use #12
If this is commercial and the load is rated 4500 watts at 240 and the actual voltage is 208 then you could use #12