For a commercial apartment building with a calculated load of 1135 amps.
if you had 90c terminals could you use 3 sets of 4- 600kcm aluminum in different 4" pipes (3 hots and neutral).
600kcm@380 amps x 3 =1155. Plus use the next size up breaker at 1200amps.
In my mind I thought for this situation you were not permitted to use next size up breaker, help please?
if you had 90c terminals could you use 3 sets of 4- 600kcm aluminum in different 4" pipes (3 hots and neutral).
600kcm@380 amps x 3 =1155. Plus use the next size up breaker at 1200amps.
In my mind I thought for this situation you were not permitted to use next size up breaker, help please?