Overcurrent protection over 800 amp for services

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
For a commercial apartment building with a calculated load of 1135 amps.

if you had 90c terminals could you use 3 sets of 4- 600kcm aluminum in different 4" pipes (3 hots and neutral).

600kcm@380 amps x 3 =1155. Plus use the next size up breaker at 1200amps.

In my mind I thought for this situation you were not permitted to use next size up breaker, help please?
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Who told you, you could use the next size up above 800 amps?

JAP>
No one I do not think you can per 240.4C but I did not know if that applied to UG service entrance conductors
 

jap

Senior Member
Occupation
Electrician
The rule is based on the rating of the overcurrent device, not conductors.

JAP>
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
No one I do not think you can per 240.4C but I did not know if that applied to UG service entrance conductors
Service conductor sizing is determined by the POCO not the NEC.
Are these really service entrance conductors? Anything after the service point is subject to the NEC.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Service conductor sizing is determined by the POCO not the NEC.
Are these really service entrance conductors? Anything after the service point is subject to the NEC.
Underground goes from transformer to connection doghouse POCO UG. These cables exit the connection point and terminate in the 1200 amp panel.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Misconception could have arisen from the fact that if you were dealing with a situation other than a 1200 main OCP device (like the "six circuit rule" prior to 2020)_ you could have used the 1155 rated conductors.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
ooops... missed that. Thanks infinity
I don't think he would have a gear with 90° terminations..... lugs maybe but not terminations.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
and who knows what on the other end?
The OP says it is feeding a commercial apartment building. Are you saying that a 1200 amp service in an apartment building could possibly have service equipment rated at 90° C? I can answer that, no. :)
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
The OP says it is feeding a commercial apartment building. Are you saying that a 1200 amp service in an apartment building could possibly have service equipment rated at 90° C? I can answer that, no. :)
Thank you some lug changes were suggested, but waiting on the cut sheet on the main disconnect enclosure. I strongly suspect equipment will be 75c also.
But in principle can you use next size up on breaker for main disconnect
Example incoming cable 1155 amps
Main breaker 1200
I thought that might be 240.4C issue but was unsure for services
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thank you some lug changes were suggested, but waiting on the cut sheet on the main disconnect enclosure. I strongly suspect equipment will be 75c also.
But in principle can you use next size up on breaker for main disconnect
Example incoming cable 1155 amps
Main breaker 1200
I thought that might be 240.4C issue but was unsure for services
No the next size up rule ends at 800 amps. You'll need a minimum of 1200 amps worth of conductors for a 1200 OCPD.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Thank you some lug changes were suggested, but waiting on the cut sheet on the main disconnect enclosure. I strongly suspect equipment will be 75c also.
But in principle can you use next size up on breaker for main disconnect
Example incoming cable 1155 amps
Main breaker 1200
I thought that might be 240.4C issue but was unsure for services
Changing the termination lugs does not change the temperature rating of the equipment. Very often the lugs on 75°C are rated at 90 or even 105 because they are standard lugs.
 

jap

Senior Member
Occupation
Electrician
The OP says it is feeding a commercial apartment building. Are you saying that a 1200 amp service in an apartment building could possibly have service equipment rated at 90° C? I can answer that, no. :)

Is a crimpon lug bolted to a transformer spade or bussbar a 75d connection?

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is a crimpon lug bolted to a transformer spade or bussbar a 75d connection?

JAP>
I doubt it but maybe it is, I don't know. Regardless that point is moot since in this installation the equipment on the other end is only rated for 75° C.
 