I doubt it but maybe it is, I don't know. Regardless that point is moot since in this installation the equipment on the other end is only rated for 75° C.
And what limits the service equipment to 75d C ?
JAP>
I doubt it but maybe it is, I don't know. Regardless that point is moot since in this installation the equipment on the other end is only rated for 75° C.
UL testing.And what limits the service equipment to 75d C ?
JAP>
No quite true, but for most applications yes.So no service equipment is 90d C rated even if it's a bussed structure from the breaker to a connection point with no mechanical terminal lugs?
JAP>
Most all compression lugs are rated at least 90°C, but that does not change the equipment rating. You still have to look at that.Is a crimpon lug bolted to a transformer spade or bussbar a 75d connection?
JAP>
Bolt onIs a crimpon lug bolted to a transformer spade or bussbar a 75d connection?
JAP>
You just add a 30 amp service disconnect along side the 1200 amp one and then your conductors only need to be equal to the calculated load.As Augie brought up earlier, if you have six disconnecting means you might be able to have less than 1200 amp conductor, still needs to be greater or equal ampacity as calculated load. Six disconnect rule didn't go away in 2020 NEC but they need to be in separate enclosures or separate switchboard sections.
How do you plan to connect the service conductors to the 30 amp disconnect?You just add a 30 amp service disconnect along side the 1200 amp one and then your conductors only need to be equal to the calculated load.
There are no size limitations on connections to service conductors like there are for the tap rules in Article 240.How do you plan to connect the service conductors to the 30 amp disconnect?