What size inverse time circuit breaker should be installed for a group installation to protect the following 208 V, three-phase motors? One 7.5-HP motor, two 10-HP motors, and one 15-HP.
Step 1
Find the FLC for each motor
From NEC Table 430.250:
• 7.5 HP motor: 24.2 A
• 10 HP motor: 30.8 A
• 15 HP motor: 46.2 A
Step 2
size
Calculate the maximum allowable circuit breaker
Apply NEC 430.52:
• Maximum breaker size
= (2.5 X FLC of largest motor) + sum of FLCs of otl
=(2.5×46.2 A) + 24.2 A + 30.8 A + 30.8 A
= 115.5 A + 24.2 A + 30.8 A + 30.8 A
• Maximum breaker size = 201.3 A
Step 3
Select the standard circuit breaker size
Solution
The size of the inverse time circuit breaker should be 225 A.
But in the answer they give me 200 A
May be I’m doing something wrong I just copy and paste the question to google, and google give a 200 A answer, But google give me 42 A for the 15 HP 208V 3-phase motor, I check the table 430.250 and shows 46.2
Thank you
Step 1
Step 2
size
Apply NEC 430.52:
Step 3
Solution
Thank you