overcurrent protection
kevinmcc4
I have a yogurt machine that has a nameplate rating of 18a min. ckt amp and a 25 amp max brkr protection can I run # 12 conductors by table 310-16 or do I need to have 10awg wire the motors in the machine have thermals on the contactors.
how is the machine connected to it's branch circuit ? hard wired ?
there could possibly be varying opinions on this but, to me, if it's cord and plug connected and you used a 25 amp, then I would think that you needed a #10 wire and 30 amp receptacle. With a receptacle there, on a 25 amp breaker, it would be available for apparatus rated more than the 20 amp #12 limitation.