Why is the overcurrent relay's - CT (Wired from the CT to the O/C relay), placed before a circuit breaker and why not it is connected after a breaker. this has been noticed with any bay -either the line bay or transformer bay.
rich -It can be done either way as the 50/51 relays are non-directional. ---
rich ---- The polarity of the current transformers is not important as long as they are all in the same direction. ---
rich -
Is this a Yogi Berra-ism? If so, it was a good one.:smile:
cf
I does not matter. More the most suitable location is before the feeder ACB.Why is the overcurrent relay's - CT (Wired from the CT to the O/C relay), placed before a circuit breaker and why not it is connected after a breaker. this has been noticed with any bay -either the line bay or transformer bay.
Why is before the "feeder ACB" a better location?---More the most suitable location is before the feeder ACB.
Why is before the "feeder ACB" a better location?
cf
It includes the circuit breaker in the feeder zone of protection and the 87 which is usually located on the feeder side of the breaker includes the breaker in its zone of protection providing an overlap of protection for the circuit breaker. The overlapping zones of protection is the ideal way to provide complete protection for equipment.