Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Does the connection of the grounded conductor to the grounding electrode conductor (system bonding jumper) need to be made in the disconnect switch where the overhead electric service enters the disconnect switch?
My reason for asking…..
I have a project for an outdoor park where we are taking OH service from the utility company at a backboard to be located adjacent to the utility companies’ pole. This utility company pole is as far as the they will come into the property with the OH 3 phase service. We will receive the 200A service from the power company terminate in a disconnect and run this OH to a shed about 30-40 yards away. The issue I am running into is Quad Plex only comes with the 4 wires plus messenger cable. If I ground the service at the first disconnect I need the 3 phase conductors, a neutral and a ground installed to the out buildingper 250.32. If I do not bond the neutral at the first disconnect, I can just run 3 phase conductors plus a neutral OH to the shed and make the main bonding connection at the panel in the shed and establish the GES there.
This seems like such a simple thing as I am sure this is done frequently so I am missing something. I spoke to a guy with Cooper Electric who confirmed their quad-plex does not have a ground wire included. He suggested adding a separate ground wire and running it with the quadplex????
Any problems with this/Suggestions/do’s/don’ts? I do not do much OH work so need to be sure.
Thanks for looking!
My reason for asking…..
I have a project for an outdoor park where we are taking OH service from the utility company at a backboard to be located adjacent to the utility companies’ pole. This utility company pole is as far as the they will come into the property with the OH 3 phase service. We will receive the 200A service from the power company terminate in a disconnect and run this OH to a shed about 30-40 yards away. The issue I am running into is Quad Plex only comes with the 4 wires plus messenger cable. If I ground the service at the first disconnect I need the 3 phase conductors, a neutral and a ground installed to the out buildingper 250.32. If I do not bond the neutral at the first disconnect, I can just run 3 phase conductors plus a neutral OH to the shed and make the main bonding connection at the panel in the shed and establish the GES there.
This seems like such a simple thing as I am sure this is done frequently so I am missing something. I spoke to a guy with Cooper Electric who confirmed their quad-plex does not have a ground wire included. He suggested adding a separate ground wire and running it with the quadplex????
Any problems with this/Suggestions/do’s/don’ts? I do not do much OH work so need to be sure.
Thanks for looking!