If the point of attachment is installed by the contractor then it is covered by the NEC.
Regardless the sag in the conductors could hit the ground and it would not be an NEC issue.
Whether or not placement of the POA should make clearance of middle of the overhead span comply with NEC could be debatable but clearances at the point of
No debate, 90.2(B)(5)(a) is very clear.
I don't know what clearances are for this install in NESC but would bet that 8 feet would not be allowed.
I agree, but not all utilities followed the NESC in 1953.
No one should take this wrong, I am not saying service conductors at 8' above grade are a good thing.
IMO growler summed it up nicely, this has little to do with code and much to do with customer perceptions ........ and making money as well.
growler said:
Is it really all that hard for electricians to understand that a "home inspection" is not a "code inspection".
Items listed on a "Home Inspection Report" are item of concern for the home inspector because he thinks they may have a negative effect on the home value or pose a problem for the buyer.
Even if you get the AHJ to agree to grandfather in the service height it still may not satisfy the home inspector or the buyer.
When you buy a house you may not be satisfied with code minimum and it all depends on how much you are willing to spend to get something better.
Why turn down down work when it's more profitable to see how much it will cost to raise that sucker.