Overhead Service wire sized from 90 c or 75 c table ?
This is a wet location so the-2 conductor can be sized according to it's 90° C ampacity.
I looked. You are correct. Thanks for pointing me in the right direction!
The only time -2 has to go back to 75 degrees is if it's in contact with oil.
From Southwire;
THWN-2- Wet or dry locations not to exceed 90° C or locations not to exceed 75° C when exposedto oil
From Southwire;
THWN-2- Wet or dry locations not to exceed 90° C or locations not to exceed 75° C when exposed to oil
Good to know. Encore has similar data sheet:
Applications:
Type THHN/THWN-2 building wire is intended for general purpose applications as defined by the National Electrical Code (NEC).
Type THHN/THWN-2 is permitted for new construction or rewiring for 600-volt applications. Applications requiring Type THHN
or THWN-2: the conductor is appropriate for use in wet or dry locations at temperatures not to exceed 90°C or not to exceed
75°C in oil or coolants
. Applications requiring Type MTW: the conductor is appropriate for use in dry locations at 90°C, or
not to exceed 60°C in wet locations or where exposed to oils or coolants. Applications requiring Type AWM: the conductor is
appropriate for use at temperatures to not exceed 105°C in dry locations.
I wonder if this is addressed in the NEC?