quogueelectric said:I see what you are talking about now A bus detail seems to be behind the threaded plate of the breaker connection thereby the bolt socked up tight into the breaker contact and the buss detail was just sitting loosely behind it with the bolt running through the unthreaded hole of the bus detail. NICE!!!!
I just ran into almost the same scenario at an apt. building recently. Goofy voltages in one unit pointed to a neutral problem. I found what appeared to be a loose neutral bar connection in the switchgear. You could tell by the damaged screw head that someone tryed repeatedly to crank it down. After staring at it for 5 minutes, on my second trip back with building owner next to me... I finally realized this small screw was threaded in from the front of the switchgear, instead of the back like the rest of the screws holding the equipment together. (factory mistake from 50 years before!) This created the same situation where the screw was threaded tight into the first peice of metal it passed thru, then just passed thru the unthreaded busbar below it... Everything sure appeared to be tight. I wonder how many appliances were toasted over the years.