We had a project where the utility service switch had ground fault protection as it was 480/277V and high current. The 702 generator was specified as a SDS (with GFP) and the open transition transfer switch was 4 pole. This would allow the GFP to function properly.
The ATS showed up from ASCO with overlapping neutral contacts, to maintain the neutral connection momentarily (in parallel) while the phases transfered, then the neutral disconnects from the "other" source and remains only connected to the phases and neutral of the "preferred source"
http://www.ascopower.com/
What are your thoughts regarding the momentary parallel connection of the neutral and thus the upstream n-g bond for each SDS. Does this violate Article 250 since there are now parallel n-g bonds.
I think it is acceptable in the same way a closed transition switch momentarily violates the interlock requirements found in 700, 701 and 702.
The ATS showed up from ASCO with overlapping neutral contacts, to maintain the neutral connection momentarily (in parallel) while the phases transfered, then the neutral disconnects from the "other" source and remains only connected to the phases and neutral of the "preferred source"
http://www.ascopower.com/
What are your thoughts regarding the momentary parallel connection of the neutral and thus the upstream n-g bond for each SDS. Does this violate Article 250 since there are now parallel n-g bonds.
I think it is acceptable in the same way a closed transition switch momentarily violates the interlock requirements found in 700, 701 and 702.