What does overloading do to power fuses? For example, a 300E fuse has a pickup of around 660 amps. I'd like to have 6 hours of 330 amps loading during contingency switching. This still leaves my with 200% for short load time inrush.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I‘m not going to look at the curve to see any times...
but short answer is it weakens them.
doing this continually eventually get the fuse weak enough that it won’t hold its characteristics any longer.
fuse manuf. call this “sneak out”
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I‘m not going to look at the curve to see any times...
but short answer is it weakens them.
doing this continually eventually get the fuse weak enough that it won’t hold its characteristics any longer.
fuse manuf. call this “sneak out”


S&C hints that it won't with their SM and SMU fuses- but chances are it be the case.

Another thing I've read is that it shifts the whole time current curve...
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
S&C hints that it won't with their SM and SMU fuses- but chances are it be the case.

Another thing I've read is that it shifts the whole time current curve...
If it weakens it, it has to shift it and reconfigure the curve..
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
If it weakens it, it has to shift it and reconfigure the curve..


Even if it doesn't weaken it, the heat alone can still shift the curve?

Overloading with either type of element construction can result in loss of coordination with other protective devices because all published melting time-current characteristic curves are based on no preloading. The excessive preloading produced by overloading in accordance with the values listed in Tables 1 through 8 causes a reduction in melting time by as much as 70% of the published values.

 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Any overloading which causes annealing in the silver or other fuse metals will shift the curve
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
What does overloading do to power fuses? For example, a 300E fuse has a pickup of around 660 amps. I'd like to have 6 hours of 330 amps loading during contingency switching. This still leaves my with 200% for short load time inrush.
Most mainstream manufacturers give I2t curves
 