Why are the heater coils on the load side of the power contacts -- vs the line side (above the contacts)?
Why are the heater coils on the load side of the power contacts -- vs the line side (above the contacts)?
It could be a safety thing, when they trip there is no power applied to them.
Lou
Over loads are only there to protect the motor, they only have to be in series with the motor load to do this, so in respect they could be in the circuit anywhere, the only protection device that needs to be at the source of a circuit is the short circuit and ground fault device, as many motors had the overloads built right in the motor so the breaker feeding a motor circuit is only used for SCGF's this is why we can have smaller conductors on a motor circuit protected by a larger rated breaker.