You are stating two scenarios here.jwilsonjr said:snip....
The overload trips even if the disconnect to the motor is shut off and the motor is disengaged from the conveyor system so there is no mechanical load on the motor
... snip
1) the motor disconnect is opened
2) the motor mechanical load is disconnected
If it is still tripping with a motor disconnect opened downstream, it can ONLY be the conductors or a termination somewhere between the OLR and the disconnect.
If it is tripping when the motor disconnect is closed but the mechanical load is removed, it may be related to harmonics causing too much heating in the OL thermal sensors. You may have a number of issues there, I have seen it happen; i.e. inductive coupling from another load (or the other motor), capacitance in the cables causing the drive output to mis-fire, all kinds of things. It may be something that can be solved with load reactors if you don't have them. I always recommend load reactors on drives with multiple motors because I have seen a lot of screwy things like this. Often times it damages the VFD as well.
Describe the entire circuit in more detail if you have the time.
By the way, it couldn't have been ambient temperature because the SSOL was tripping too and they are all ambient insensitive.