I don't get many Square D panels around here, but I got one today that I have to add a couple of circuits to. Shame on Square D for making a 30 circuit panel with only 30 neutral spaces. This one is loaded and with Romex. Whoever did the install did a nice neat job except for putting two and three conductors (neutrals and grounds) in each neutral bar hole. Every space is used. So, my question is (and I should know this), can I take maybe six #14 grounds off and pigtail them to a single piece of #14 and land that on a neutral bar? Probably even better if I installed a new ground bar to the can someplace like was supposed to be done in the first place.

-Hal
 
  • Like
Reactions: J2H
So, my question is (and I should know this), can I take maybe six #14 grounds off and pigtail them to a single piece of #14 and land that on a neutral bar?
Absolutely, yes. All the 14s with one 14, all the 12s and 14s with one 12, etc.

You could do that with every EGC in the panel with one wire large enough.
 
Best option would be add a ground bar.
Question I have is, How far back in the code did they allow the N and G to be under a single termination in the main panel? See it a lot in older 70 and 80's installations. The better ones would actually have the associated N/G combined, but do come across ones with non-associated N/G under a single termination.
 
My favorite is old, full panels with stacked neutral bars. You go to add a circuit and can just make out an unused terminal...in the back bar!
 