Agreed. Please provide any data on overload characteristics of pole top transformer with respect to time,cooling period thereafter etc., if you have any. Thanks.
You can run them up to about 300% for very short periods. I have been amazed at some of the transformers I have found that have survived for a very long time with severe overloads. I know the older ones are quite durable but I suspect the newer ones are not over-built as much.
Anyway, you have to factor in maximum loading prior to the overload, initial loading profile, temperature ambients and ratings, duration of overload, acceptable loss of life, etc. There are publications that cover the specifics but some generic examples:
Normal life expectancy with 1 hour overload:
For 90% initial load: 140% loading permitted
For 70% initial load: 154% loading permitted
For 50% initial load: 160% loading permitted
Normal life expectancy with 4 hour overload:
For 90% initial load: 112% loading permitted
For 70% initial load: 117% loading permitted
For 50% initial load: 119% loading permitted
0.25% life loss per occurance with 50% Initial loading:
1 hour overload: 191% loading permitted
4 hour overload: 138% loading permitted
1.0% life loss per occurance with 50% Initial loading:
1 hour overload: 200% loading permitted
4 hour overload: 153% loading permitted
0.25% life loss per occurance with 100% Initial loading:
1 hour overload: 169% loading permitted
4 hour overload: 132% loading permitted
1.0% life loss per occurance with 100% Initial loading:
1 hour overload: 192% loading permitted
4 hour overload: 148% loading permitted