- Location
- Placerville, CA, USA
- Occupation
- Retired PV System Designer
I have a problem with their attempt to rationalize the neutral of a high leg delta with the same rubric that covers the center point of a wye: it is dependent on the way that the phase conductors are used.Whether or not a conductor is "neutral" has to do with where it is connected in the system, not whether or not it is grounded. If grounding a phase conductor made it the neutral, corner-grounded delta systems would be even more confusing than they already are.And what about high-impedance-grounded or ungrounded systems? :blink:
FPN: At the neutral point of the system, the vectorial sum of the nominal voltages from all other phases within the system that utilize the neutral, with respect to the neutral point, is zero potential.
(Disclaimer: I did not know any of this until I started frequenting these forums a few months back. Thanks for the lessons, everybody.)
The formal definition provides a list, which is fine. The informational note, IMHO, goes off the deep end. Strictly speaking, it means that if you attach a 208 volt load between the high leg and the center tap, the center tap would no longer be a neutral because you would now have to include the 208 volt phase vector in the vector sum.
And it means that if you have a 208Y/120 and you only bring two of the three phase conductors to the service, the center point is no longer a neutral, contrary to the list in the formal definition.
Sometimes it is better just to rely on using a list and not try to justify it in a "simple" way.