roninblayd
New member
We are preparing to upgrade a service at a 6 unit condo building located in Chicago and of course are trying to minimize costs. We calculated a demand load of 410A, so unfortunately need a 600 amp rated disconnect. My question is: if we use a fusible disconnect, can we size the fuse for let's say 500amps (if 500 amp fuses are available) to protect two sets of parallel 3/0 service entrance conductors? This is my reasoning for not installing a full sized 600amp service with parallel 250 or 350kcmil conductors. The chicago inspectors do not like the smaller conductor allowance per table 310.15(B)(6) and even though the calculated load is only 410 amps, say that we should install a full 600amp service.
Reasoning: 3/0 conductors are rated at 225 amps for residential services in both chicago and nec. parallel 3/0 would provide 450amps. next size standard fuse is 500 amps and 600 amp rated disconnect is the only size after 400 amps. Using parallel 3/0 also allows us to use #2awg grounding electrode conductor in 3/4" conduit and considering that the water meter is very far away and inconveniently located, saves considerably over the 1/0 or 2/0 if we had a fully sized 600 amp service.
Are 500amp fuses readily available? Is what I propose acceptable per code? What is normally done? I can always fudge the AC loads which are not even currently exisiting so the calculated load is less than 400amps but prefer not to do that. We just planned for the near future where owners are going to install AC's.