If you going to use the VFD as the motor protection, make sure you program the motor FLA and not use the default.
What is the application?
I have installed very oversized drives on overhauling loads such as mining conveyors so the drive doesn't trip on a bus overvoltage fault. The motor load suddenly goes to generator load as the the loaded conveyor overcomes gravity or something else equally important.
Hope that helps and good luck