Williamwallace
New User
- Location
- New York
- Occupation
- Telecom
I have 60A breakers with a form factor that uses more space in the panel than the 3 poles it occupies. (Don’t ask - data center RPP) Anyway to regain the lost space I want to simply replace the breakers with 50A units that use only 3 poles. Is there any reason I need to replace the branch circuit wire or recepatcles that are rated for 60A? (Load will never even approach the 50A limit) thanks.