was doing a mall store recently and noticed the 480 was around 510. I was just there helping finish up, so I didn't mess with any of the trannies (the 208 was a little high). At what point do you feel responsible to start fiddling with the taps ? 10% ?
About the only time I have adjusted taps (Manual Taps) is when transformers with taps set for 480 VAC were installed in building utilizing 465 VAC.
was doing a mall store recently and noticed the 480 was around 510. I was just there helping finish up, so I didn't mess with any of the trannies (the 208 was a little high). At what point do you feel responsible to start fiddling with the taps ? 10% ?
What piece or general types of equipment call for that size of service ?
In Washington DC, PEPCO delivers 480 VAC, in the burbs commercial services are delivered at 465 VAC.
In addition during the summer high peak periods in the outer limits of the service area we have measured 432 VAC, with transformers tapped for 480 VAC output voltage is low.
was doing a mall store recently and noticed the 480 was around 510. I was just there helping finish up, so I didn't mess with any of the trannies (the 208 was a little high). At what point do you feel responsible to start fiddling with the taps ? 10% ?
Is 465 the target they want to achieve and why?
Around here pretty much all 480 services will measure around 500 with little or no load, 208 volt services will usually read about 215, 240 volt services will usually be around 250 with little or no load. Sometimes in cities or towns if multiple services are fed from one transformer you will see lower voltages, but not clear down to 432 at service equipment on a 480 volt system.