I think the heat strips kick in every time outdoor unit goes into defrost?optional
I think the heat strips kick in every time outdoor unit goes into defrost?optional
Is the Hot tub really included in the general loads with the first 10@100% and 40% remainder?
Line 220.82 qty VA VA Extended 1 General 1700 3 5100 2 Small App / Laundry 4 1500 6000 3 Disposal 1 900 900 4 Dishwasher 1 1200 1200 5 Dryer 1 5500 5500 6 EVSE 1 7200 7200 7 Spa 1 10000 10000 8 35900 9 First 10kVA 10000 10 40% of remainder 10360 11 Subtotal (B) loads 20360 12 13 14 Heatupmp 1 7680 7680 15 Supplemental 1 20000 16 65% supplemental 13000 13000 17 Sum of HVAC (C) 20680 18 Total Load Sum of B and C 41040
Yes, also, can and will get stuck on and stop a home from cooling and create a service call... lol...I think the heat strips kick in every time outdoor unit goes into defrost?
They can.I think the heat strips kick in every time outdoor unit goes into defrost?
In order for it to bring heat into the house, the coil needs to be colder than the outside air so it will absorb heat from that air. Chances are it will be cold enough for frost to form on the coil when it runs.The heat pump around my area will never freeze up. It gets 32 maybe one day.