P.V. system installed on a standing seam roof. The roofing is painted or coated.
?'s Is the roof likely to become energized & does it need to be bonded?
Thank you in advance. :thumbsup:
 

Carultch

Senior Member
Location
Massachusetts
P.V. system installed on a standing seam roof. The roofing is painted or coated.
?'s Is the roof likely to become energized & does it need to be bonded?
Thank you in advance. :thumbsup:

I'm curious to know how one would actually expect to bond the metal roofing. S-5! clamps are specifically designed with a rounded point set-screw, so they do not damage the protective coating on the roofing material. Any way that you would attach a grounding connection would have to cut through the coating, unless you have an unpainted roof like galvalume, bare copper, or zinc-coated copper.

And if you do damage the coating on the metal roof, you ruin the leak protection performance of the roofing system.

The only way I could see to bond the roofing panels, is to do so under the ridge cap, where it is already protected from the rain.
 

rcarroll

Senior Member
Thanks. But, in your opinion, is the roof "likely to become energized"? This is the first time I've come across this.
I believe the building is wood framed. A metal building, I wouldn't have a question.
 
I think bonding a metal roof would be silly. Here are my reasons:

1. I have never heard of anyone having to do it, therefore the issue does not exist (kinda joking here)

2. The roof is already bonded by the zillions of S5 clips and fasteners.

3. We install electrical on metal buildings all the time, lights, plugs, RTU's, and don't go out of our way to bond the roofing or siding. Why should PV be different?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I've been through this conversation a couple times with AHJs but have never actually done anything to specifically bond the roof or ultimately been required to. The sticking point is: okay, say I agree the roof needs to be bonded, can you show me a product to bond it with?

With that said, I would not take electrofelon's bet unless I had $10 and sandwich I needed to get rid of.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
this is like arguing over whether sheet metal studs should be bonded.

Personally, I think all the zip screws do a perfectly acceptable job of bonding them together, even though the code does not allow sheet metal screws to be used for this purpose. So your first problem is how do you connect all the pieces of sheet metal together before connecting some kind of EGC to it.
 