Texas does not require Vacancy/Occupancy sensors for Residential single dwelling.
Edit: Depending on where you're located though, Texas has adopted the 2017 NEC.
Under the 2017 NEC 422.31 (Disconnection of Permanently Connected Appliances):
(A): Rated at Not over 300 VA or 1/8 HP: For permanently connected appliances rated at not over 300VA or 1/8HP, the branch circuit overcurrent device shall be permitted to serve as the disconnecting means where the switch or circuit breaker is within sight from the appliance or is lockable in accordance with 110.25.
The bold section is new, and if you agree that a paddle-fan is an appliance, and you cannot see the switch as it's on the other side of the wall, you may have a leg to stand on.
Doesn't the paddle fan have an integral on/off switch?