Painfully basic question on wires allowed under lugs in disconnect

Status
Not open for further replies.

David Goodman

Senior Member
Location
Pahrump, NV, USA
I have come across several electric furnace installations where the disconnect load lugs were used to make connections for the blower motor and multiple electric heat strips.

Attached is a specification sheet on a very common disconnect.

When looking at the Wire Range Table in the upper right corner, I would not read this as more then one conductor allowed under a lug.

For instance, you could have a single stranded 14 AWG to 2 AWG conductor under a load lug.

Please let me know if I am reading this correctly.
 

Attachments

  • 5ccaf388-daae-44eb-af9d-4f0cfb34ccfe.pdf
    142.5 KB · Views: 0
I have come across several electric furnace installations where the disconnect load lugs were used to make connections for the blower motor and multiple electric heat strips.

Attached is a specification sheet on a very common disconnect.

When looking at the Wire Range Table in the upper right corner, I would not read this as more then one conductor allowed under a lug.

For instance, you could have a single stranded 14 AWG to 2 AWG conductor under a load lug.

Please let me know if I am reading this correctly.

You are reading it correctly.
1 conductor only. if it allowed 2 it probably would read (2) 14-2
 
I have come across several electric furnace installations where the disconnect load lugs were used to make connections for the blower motor and multiple electric heat strips.

If the wiring is an integral part of the furnace then the NEC does not apply.
 