Painfully basic question on wires allowed under lugs in disconnect
David Goodman
Pahrump, NV, USA
I have come across several electric furnace installations where the disconnect load lugs were used to make connections for the blower motor and multiple electric heat strips.
Attached is a specification sheet on a very common disconnect.
When looking at the Wire Range Table in the upper right corner, I would not read this as more then one conductor allowed under a lug.
For instance, you could have a single stranded 14 AWG to 2 AWG conductor under a load lug.
Please let me know if I am reading this correctly.
  • 5ccaf388-daae-44eb-af9d-4f0cfb34ccfe.pdf
You are reading it correctly.
1 conductor only. if it allowed 2 it probably would read (2) 14-2
If the wiring is an integral part of the furnace then the NEC does not apply.