I just started with a company that is installing conduit in a hospital,
they are using green, orange, and blue conduit. My question in if the conduit
is painted how can you use it as an effective ground-fault current path?
(the conduit is painted end to end) by the way it EMT. all replays are greatly appreciated
 
If you're using set-screw connectors, you'll have a good ground. If you're pulling a ground anyhow, it's basically only bonding. I wouldn't get too worked up over it. Go ahead and sand off the paint at each fitting, and see how long it takes your foreman to jump your case. :)
 
stickboy1375 said:
How does the paint hold when making bends? I'll I envision is the paint falling off after making a 90* bend...:)

It's more than just painted, it's some type of a chemical process although I don't know if anodized would be the correct term for the finishes on this line from Allied tubing.

We have been using the red Fire Alarm EMT for a number years now and there is no special considerations to installing it verses regular EMT.

For a while it was a little more expensive but now we are buying for the same price as plain EMT.

Roger
 
The allied EMT:

http://www.alliedtube.com/electrical-raceways/conduit/blue-emt.asp

(from their website)

Red Fire Alarm EMT Allieds Fire Alarm EMT with a bright red topcoat, FIRE ALARM EMT provides instant identification of fire alarm circuitry.


This Features:
Hot-galvanized for durability
Quick and easy installation
Damage-resistant strength combined with ductility for easy bending
E-Z Pull interior finish provides a smooth raceway for wire-pulling
Excellent EMI shielding characteristics
Full code and standard compliance; UL listed and labeled
Trade sizes from 1/2" through 2".
 