I think we should learn how to spell "receptacle".
Painters will remove the faceplates from recepticle faceplates before painting.
Taking off the faceplates exposes live conductors.
Should they be required to de-energize, and lock out and tag out the circuits involved based upon NFPA 70E?
Your not working with live parts unless you cross the prohibited approach and are not working near live parts unless you cross the restricted approach boundary. For a 120 volt receptacle both of these boundaries are listed as "avoid contact" (do not touch) in Table 130.2(C). The removal of the device covers is not working on or near live parts, the only issue would be arc flash protection, however the protection category would most likely be "0" requiring only long pants and long sleeve shirt of non-melting fabric.
why require faceplates at all?
Because OSHA may fine the employer of exposed employees up to $7,000.
The definition from the standards:
"Exposed. (As applied to live parts.) Capable of being inadvertently touched or approached nearer than a safe distance by a person. It is applied to parts not suitably guarded, isolated, or insulated."
DUH!!! If it's a REPAINT, the painter's responsible for safe removal. There's no electrician there.Uh, people have been know to REpaint rooms....
I think we should learn how to spell "receptacle".
............I think the the solutions are, ......... or ensure that all the painters are also "qualified electrical workers" ..............