Then you possibly cross the boundaries of marking it as being an ungrounded conductor, plus you really confuse the untrained when you have a "marked" conductor on the neutral bar:happyyes:
Simple circuit tracers send a signal thru the grounded conductor as well as thru the ungrounded conductor.
There is a border between marked grounded wires for association purposes and re-identified white wires for power feeds in switch loops. If you follow the rules crossing the border is forbidden.
You are only allowed to re-identify white wires for switch loops when they are contained in cables. Presumably there are few if any power rated cables that contain more than one white wire. When one or more neutrals are contained in a cable you probably do not have to be superman to associate the neutrals and hots.
The only time that you need to mark neutrals for association is when they are not in cables.
I don't see any overlap:?
I am familiar with Fox and Hound telephony tracers, CAT5+ tracers and cable identifiers, and Ideal de/energized circuit tracers
Sure tracers send the signal through both the neutral and the hot, if they are connected between the neutral and the hot, but I am unfamiliar with any that can distinguish one neutral conductor connected to a neutral bar from any other.
Even fairly expensive circuit tracers have difficulty unambiguously determining the correct breaker, giving similar readings for breakers connected to wires sharing the same raceways.
Can you give me a model number that distinguishes neutrals while still connected to the neutral bar?